Re: [CCAMP] New Version Notification for draft-vallin-ccamp-alarm-module-01.txt

stefan vallin <stefan@wallan.se> Mon, 06 November 2017 10:38 UTC

Return-Path: <stefan@wallan.se>
X-Original-To: ccamp@ietfa.amsl.com
Delivered-To: ccamp@ietfa.amsl.com
Received: from localhost (localhost [127.0.0.1]) by ietfa.amsl.com (Postfix) with ESMTP id 6A4A313FB52 for <ccamp@ietfa.amsl.com>; Mon, 6 Nov 2017 02:38:38 -0800 (PST)
X-Virus-Scanned: amavisd-new at amsl.com
X-Spam-Flag: NO
X-Spam-Score: -2.599
X-Spam-Level:
X-Spam-Status: No, score=-2.599 tagged_above=-999 required=5 tests=[BAYES_00=-1.9, DKIM_SIGNED=0.1, DKIM_VALID=-0.1, HTML_MESSAGE=0.001, RCVD_IN_DNSWL_LOW=-0.7] autolearn=ham autolearn_force=no
Authentication-Results: ietfa.amsl.com (amavisd-new); dkim=pass (2048-bit key) header.d=wallan-se.20150623.gappssmtp.com
Received: from mail.ietf.org ([4.31.198.44]) by localhost (ietfa.amsl.com [127.0.0.1]) (amavisd-new, port 10024) with ESMTP id BCYatXSTEn_s for <ccamp@ietfa.amsl.com>; Mon, 6 Nov 2017 02:38:36 -0800 (PST)
Received: from mail-lf0-x235.google.com (mail-lf0-x235.google.com [IPv6:2a00:1450:4010:c07::235]) (using TLSv1.2 with cipher ECDHE-RSA-AES128-GCM-SHA256 (128/128 bits)) (No client certificate requested) by ietfa.amsl.com (Postfix) with ESMTPS id 3647D13FA82 for <ccamp@ietf.org>; Mon, 6 Nov 2017 02:38:35 -0800 (PST)
Received: by mail-lf0-x235.google.com with SMTP id n69so9967823lfn.2 for <ccamp@ietf.org>; Mon, 06 Nov 2017 02:38:35 -0800 (PST)
DKIM-Signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=wallan-se.20150623.gappssmtp.com; s=20150623; h=mime-version:subject:from:in-reply-to:date:cc:message-id:references :to; bh=hWOVt0ILKIf9Vq+w1OD2p/CgKWogXRqnnBafx0mO2RE=; b=rUh7u2a0r9PVCEFyjPR2p7ZMNE56KrAHygRzg8cqflL2jlU1HSIcaa8tS+1XPIXLLs hLd18gIEISUR3qOBjN21uLSGfPhVtzIpBNtkFv64a10voxX8vOCsAfxk3STwU2vqgnsY kYm7bpzE4zsoLo0c/vSSun3X+5yNNqYFL/lguXKuITQfzGx8K5/vg6O/OvctlwzEKc8e IC2nIaT4R6lnR75sbkZZNIzpSskSmFx27/Y7kKWGs2DSflvVuJwre7AMSp6Wv9yckf0u yCKUpcN2bhVt1Qq96kjjsKiy8dedQS/SQD/5oP29he/B8dDSrlm3gqrMCvNpBOhJ6Ph4 KIOw==
X-Google-DKIM-Signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=1e100.net; s=20161025; h=x-gm-message-state:mime-version:subject:from:in-reply-to:date:cc :message-id:references:to; bh=hWOVt0ILKIf9Vq+w1OD2p/CgKWogXRqnnBafx0mO2RE=; b=h0bSIh4k3deuUzDAW8jIOzpfTkg2L0MwTuqqGHGCvfoBuRd3twKbMwHHLUZCzyOyWw WCJBnCA48RogmFNXqvEliGkh+wu683f9pLeQpOgGuMjOGnr0xdNDNbjpyWb1bGUPbAtr ycC1kKfiW1CcPXyedwBOj82v2YCwmqMBxGhj6wERNVOr0k0kuwFwCu7pULGanXPsoiV5 xZlhZxZCvBOQhSCKbQhQYTkLN8s/12ejzt+gQPCsd56iz+5hiVhp8wESrmGB7NPaA5Nk hY24XGc+j8ipzQzi3dxZvuC07jw7VCoT9FC0bT54YIFEKtiOw5HGeI/n17+NZRXVMkbH ykDg==
X-Gm-Message-State: AMCzsaVL48WxBDnV6LoZ1SEeWFUns277cBFsEDXvDI8HgMuyB1fZZlRu MIBBUcgGp4U5tML/P805x1bOWNxK/js=
X-Google-Smtp-Source: ABhQp+TSbiP7VoLlPMgGys6JMpan02HzzdWXsj/110J3MF7q5587+NkizjnVHoBQ37DRNMWqtm92kg==
X-Received: by 10.46.15.2 with SMTP id 2mr5790876ljp.30.1509964713356; Mon, 06 Nov 2017 02:38:33 -0800 (PST)
Received: from [192.168.99.130] ([195.234.15.132]) by smtp.gmail.com with ESMTPSA id s16sm2523580ljd.77.2017.11.06.02.38.32 (version=TLS1 cipher=ECDHE-RSA-AES128-SHA bits=128/128); Mon, 06 Nov 2017 02:38:32 -0800 (PST)
Content-Type: multipart/alternative; boundary="Apple-Mail=_D8DED8B7-4EBF-4791-BF4D-41CF146C03A9"
Mime-Version: 1.0 (Mac OS X Mail 9.3 \(3124\))
From: stefan vallin <stefan@wallan.se>
In-Reply-To: <BD6D193629F47C479266C0985F16AAC7F0675134@ex-mb1.corp.adtran.com>
Date: Mon, 06 Nov 2017 11:38:29 +0100
Cc: "ccamp@ietf.org" <ccamp@ietf.org>, JOEY BOYD <joey.boyd@adtran.com>
Message-Id: <7215B14E-CA90-4EDB-BE4C-594EC3FA0B1B@wallan.se>
References: <BD6D193629F47C479266C0985F16AAC7F0675134@ex-mb1.corp.adtran.com>
To: NICK HANCOCK <nick.hancock@adtran.com>
X-Mailer: Apple Mail (2.3124)
Archived-At: <https://mailarchive.ietf.org/arch/msg/ccamp/0pMsf7lDqeV6BfpEwbtlqpzB3nw>
Subject: Re: [CCAMP] New Version Notification for draft-vallin-ccamp-alarm-module-01.txt
X-BeenThere: ccamp@ietf.org
X-Mailman-Version: 2.1.22
Precedence: list
List-Id: Discussion list for the CCAMP working group <ccamp.ietf.org>
List-Unsubscribe: <https://www.ietf.org/mailman/options/ccamp>, <mailto:ccamp-request@ietf.org?subject=unsubscribe>
List-Archive: <https://mailarchive.ietf.org/arch/browse/ccamp/>
List-Post: <mailto:ccamp@ietf.org>
List-Help: <mailto:ccamp-request@ietf.org?subject=help>
List-Subscribe: <https://www.ietf.org/mailman/listinfo/ccamp>, <mailto:ccamp-request@ietf.org?subject=subscribe>
X-List-Received-Date: Mon, 06 Nov 2017 10:38:38 -0000

Hi Joey and Nick!
Thanks for your comments, really good ones.
See answers inline

br Stefan and Martin

> On 03 Nov 2017, at 16:50, NICK HANCOCK <nick.hancock@adtran.com> wrote:
> 
> Hi!
>  
> We have some questions and comments on the concept of shelving and how it is intended to be implemented and used within the YANG Alarm Module.
>  
>  
> 1. Alarm shelving and alarm suppression
>  
> 3GPP TR 32-859 based on a presentation from ANSI/ISA 18.2 defines alarm shelving as one method of alarm suppression, the others being out-of-service alarms and alarms suppressed by design.
>  
> You effectively combined out-of-service alarms with alarm shelving deciding not to have separate lists for out-of-service alarms and shelved alarms. 3GPP TR 32-859 also defines ‘a time limit for shelving’, but such was not included as part of alarm shelving in the YANG Alarm Module. What was the reasoning behind these decisions?
Answer:
Correct, we did let shelving cover out of service as well. You could just create a shelf named OOS if you like.
Actually in an early version of this module there was a timer as well. But we removed it.
The shelf is configuration data. The timer feature would then make the server change its configuration autonomously which is not the intent of configuration.
Therefore we consider the management system (NETCONF client) being responsible for managing the timer.

>  
>  
> 2. Shelving and un-shelving alarms
>  
> This is our understanding of how alarms are shelved and un-shelved in the YANG Alarm Module:
>  
> An alarm will be shelved by a system when the alarm meets the ANDed criteria of one or more entries in the list ‘shelf’.
>  
> So to shelve an existing alarm within the list ‘alarm’ an operator has to create an entry in the list ‘shelf’ or modify the criteria of one or more existing entries in the list ‘shelf’, so that the existing alarm is now included in the shelving criteria as defined by all entries within the list ‘shelf’.
> And to un-shelve an existing alarm within the list ‘shelved-alarm’ an operator has to delete an entry in the list ‘shelf’ or modify the criteria of one or more existing entries in the list ‘shelf’, so that the existing alarm is no longer included in the shelving criteria as defined by all entries within the list ‘shelf’.
>  
> Is our understanding correct? 
Answer:
Yes
>  
> However: the action ‘set-operator-state’ connected to the list ‘alarm’ currently allows the value ‘shelved’ to be specified as a valid input for the leaf ‘state’. How can this be reconciled with alarm shelving as described above?
>  
> Specifically, if the operator is able to explicitly shelve an alarm by means of this action, this would mean that there would be a shelved alarm in the list ‘shelved-alarm’, for which there is no entry in the list ‘shelf’ with criteria that meet the shelved alarm. In addition, there is no corresponding action connected to the list ‘shelved-alarm’ to enable an operator to un-shelve an alarm.
Answer:
Good catch, we were not clear on the intended usage.

The set-operator-state is not intended to be used for shelving, and the “shelved” state shall only be set the by the server not by the client.
        enum shelved {
          value 4;
          description
            "Alarm shelved.  Alarms in alarms/shelved-alarms/
             MUST be assigned this operator state by the server as
             the last entry in the operator-state-change list.";
        }
        enum un-shelved {
          value 5;
          description
            "Alarm moved back to alarm-list from shelf.
             Alarms 'moved' from /alarms/shelved-alarms/
             to /alarms/alarm-list MUST be assigned this
             state by the server as the last entry in the
             operator-state-change list.";

However we lack descriptions making that clear. We should also redesign the operator-state enum into
- the settable values
- the readable values


Something like this:
typedef writable-operator-state {
  type enumeration {
    enum none;
    enum ack;
    enum closed;
  }
}

typedef operator-state {
  type union {
    type writable-operator-state;
    type enumeration {
      enum shelved;
      enum un-shelved;
    }
  }
}

So the idea is that shelving shall appear in the history of operator actions on the alarm.
But shelving is not performed by the set-operator-state.

>  
>  
> 3. Shelf criteria
>  
> A shelf defines shelving criteria and these criteria are ANDed. But each of the leafs representing the criteria is also optional, which means that it would be valid to define a shelf with no criteria.
> Since we see a valid use case where an operator wishes to shelf all alarms of a system with a single configuration, we thus believe would be very useful, if a shelf configured with no criteria would shelf all alarms.

Answer:
Your questions/comments retriggered a thought me and Martin have had around resource wild-carding and resource sub-trees.
We prefer the shelf to be explicitly configured but using a resource wild-card “*”. 
Also it should be possible to specify a resource sub-tree like “/interfaces”.

>  
> Could the authors clarify what the intended behavior would be in the case of a shelf configured with no criteria?
Answer:
No criteria would be a noop.
We suggest a resource wild-card mechanism as described above.
>  
> To define an entry in the list ‘x733-mapping’ ‘alarm-type-qualifier-match’ was used instead of just ‘alarm-type-qualifier’. Wouldn’t the use of ‘alarm-type-qualifier-match’ instead of just ‘alarm-type-qualifier’ as a shelf criterion be a better and more flexible solution?
Answer:
Good suggestion!
>  
>  
> 4. Shelving alarms for multiple resources
>  
> For maintenance purposes, it may be practical to be able to shelf all alarms for all resources associated with a given card within an equipment. In the current implementation, this would mean creating separate shelf entries, one for each affected resource located on the card. Wouldn’t it be advantageous if the criterion ‘resource’ be a leaf-list instead of just a leaf?
Answer:
Good suggestion!
>  
>  
> 5. Shelving based on perceived severity
>  
> We are aware that in some network implementations there is the requirement to be able to shelve alarms based on their severity.
>  
> The severity of an alarm is not included in the criteria of a shelf in the YANG Alarm Module. Was this considered? What are the authors view on supporting shelving based on the severity of an alarm?
Answer:
Shelving and severity does not really go well together.
Severity levels are notification-focused.
An alarm is a state on a resource and it might change state with resulting notifications, for example: major, minor, and then a clear flag for the minor alarm state.

So shelving can not really be done on severity levels.
>  
>  
> 6. Shelving an active alarm only until it is cleared
>  
> We are considering the use case, in which an operator is requiring to shelve an active alarm only until it is cleared, i.e., when the alarm is cleared, it should be automatically be un-shelved by the system.  This use case is currently not covered by the current implementation of the YANG Alarm Module, because alarms are shelved based only on the criteria defined by the entries in the list ‘shelf’, which apply independently of whether an alarm is active or cleared.
>  
> What are the authors views on supporting such a use case and how could this be implemented?
Answer:
We do not consider this to be a shelving feature. This is more a filtering function in the management system.
This is for several reasons, see above on severity levels.
Also this would make the system change its configuration (shelf criteria)  autonomously as in question #1 which is not preferable.
>  
>  
> 7. Notifications
>  
> When alarms are shelved, the system is to stop sending notifications for the shelved alarms.
> We infer that at the point in time when an alarm is shelved, no notification would be sent as the change of the ‘operator-state’ of an alarm is never notified.
>  
> We are concerned that in the case of multiple clients, some clients will not be made aware that an alarm has been shelved.
>  
> Why was an explicit ‘alarm shelved/un-shelved’ notification, which would be sent when an alarm is shelved and when it is un-shelved, not implemented in the YANG Alarm Module?

Answer:
Makes sense. Will add notifications for this.

>  
>  
> if any of these topics have already been discussed before, please point us to where we can find the discussion.
>  